al Senior Member Location Minnesota Dec 16, 2006 #1 Household generator inlet 30amps mounted outside adjacent to main service panel. Question: Does this need to be wired as a service? Thus no MN cable, #8 min CU wire etc......? Code reference?
Household generator inlet 30amps mounted outside adjacent to main service panel. Question: Does this need to be wired as a service? Thus no MN cable, #8 min CU wire etc......? Code reference?
iwire Moderator Staff member Location Massachusetts Dec 16, 2006 #2 No you do not treat a generator as a service, you might treat it as a separately derived system. The reference is in Article 100 definitions. Only a utility can supply a service, any other supply is considered a feeder.
No you do not treat a generator as a service, you might treat it as a separately derived system. The reference is in Article 100 definitions. Only a utility can supply a service, any other supply is considered a feeder.