how is it a code violation if the feeders are protected properly? i have installe many 25 kw gen sets on 200 amp panels. the service disconnect and transfer switch must of course match the 200 amp panel because in the utility postion the transfer switch carries the full panel load. in the emergency postion however typically a 25 kw gen set can only provide 86 amps or so and is protected by a 100 amp breaker. there is no code violation here as the generator and the feeders are properly protected. If the homeowner is not careful and adds too much load the ocp device will trip when it should and everything is protected. Where do you feel the code violation exists? design flaw maybe but code violation not methinks.