Customer wants a whole-house backup generator. Right now 4/O AL SEU runs from service to Main Panel with 200 Amp service. We are installing a Generac 20K with Nexus Smart Switch ATS. Length of run from generator to panel/transfer switch is less than 20'. Generac calls for the SEU to run straight into the transfer switch, and thereafter, the distribution panel. The install calls-out for a new run of the SEU to reach the transfer switch (2' longer). Generac instructions calls for 250 MCM wire. Under the most restrictive interpretation of the NEC:
1. Does the NEC require a service disconnect between the utility service and the transfer switch?
2. Does the NEC require a service disconnect between the generator and the transfer switch?
3. Am I misreading NEC 310.16, or can I run 4/O AL SEU from the utility service to the transfer switch, and then run 2.5'' pipe with 4/O THHN from the transfer switch to the generator and from the transfer switch to distribution panel?
4. Why would Generac be calling for 250 MCM?
Thanks.
1. Does the NEC require a service disconnect between the utility service and the transfer switch?
2. Does the NEC require a service disconnect between the generator and the transfer switch?
3. Am I misreading NEC 310.16, or can I run 4/O AL SEU from the utility service to the transfer switch, and then run 2.5'' pipe with 4/O THHN from the transfer switch to the generator and from the transfer switch to distribution panel?
4. Why would Generac be calling for 250 MCM?