Ryancbell121
Member
- Location
- Pennsylvania
- Occupation
- Master Electrician
I have installed generator interlock kits for 200 amp residential services and portable generators. I want to install 2 interlock kits on each 200 amp main panel of a 400 amp residential service. I will splice the conductors from the generator inlet to each panels interlock breaker.
Is there any issue with this? I read an another forum and people were saying that you have neutrals going to each panel, I dont see the problem with that since the current flows back to the generator and not on the Service neutral.
Is there any issue with this? I read an another forum and people were saying that you have neutrals going to each panel, I dont see the problem with that since the current flows back to the generator and not on the Service neutral.