hillbilly1
 - North Georgia mountains
 - Owner/electrical contractor
You are showing only one panel and one transferswitch.Tell me how I am wrong
How do you not get the picture I drew? The 10/3 from the junction boxes go to the 2 pole breakers and the neutral/ground bar.You are showing only one panel and one transferswitch.
Are you saying there’s going to be current on the service entrance conductors from the meter?You are showing only one panel and one transferswitch.
Does this picture I attach explain what I fail to see and what you’re saying?You are showing only one panel and one transferswitch.
The fix to this is to put all of the generator loads in one panel.One of my regrets about my own setup is that I went to 400 cause "I could" and the main reason I wish I didnt,, probably could have made it on 200 and would have made gen power a lot easier.
And we want to avoid connecting the two neutral busses twice, correct? They are connected thru the meter enclosure already.There are two separate neutral topics being discussed here: bonding and paralleling.
1. Bonding; a generator's neutral should not be bonded when supplying a load whose neutral is bonded, but it should be bonded otherwise.
2. Paralleling; the two neutral conductors of a single inlet supplying two panels will inadvertently be interconnecting the two neutral buses.
And have the current go back through the service entrance neutral conductor from the one 200 amp panel then into the second 200 amp panel then back on the generator feed neutral? I bet it would work but I’m sure its a violation.What if you only connected the neutral at one panel?
On second thought, that wouldn't be compliant
Well then have one inlet for each panel and then you can use two generators, correct?As I said above, the best solution is to use only one panel for desired generator loads, IMO.
Yeah no parallel path, but you would have a circuit with conductors in different cables/raceways/conduitsAnd have the current go back through the service entrance neutral conductor from the one 200 amp panel then into the second 200 amp panel then back on the generator feed neutral? I bet it would work but I’m sure its a violation.
Yes, they would function as two independent systems, as if they were two separate houses.Well then have one inlet for each panel and then you can use two generators, correct?
I’d have to ask the local utility company for one
				Correct, the generator neutral is parallel with the service neutrals to the panels.Does this picture I attach explain what I fail to see and what you’re saying?
Correct.Well then have one inlet for each panel and then you can use two generators, correct?