Yes, this post is late. I've been called off to do work. I know, the shame of it.
Minor additions to previous posts:
A lot depends on what size generation is being discussed. For box store stuff, the engine horsepower is just an advertising number, similar to
Sears 6HP compressor - and it has a 15A cord cap - yeah, ok, sure. The number is meaningless - a lie.
Once one gets above, maybe 50KW, and stays with 3ph, the generators are rated in KW, generally at .85pf, and may or may not have a KVA rating. The KVA rating doesn't matter too much, it is the KW/pf. But the KVA is needed.
The KW is a driver limitation. At rated RPM, that's all the torque the driver shaft will put on the alternator shaft. If one adds more load, the driver slows down.
The KVA is an alternator heat loading spec. As the KVA goes up, the stator current goes up, and the heat goes up. Driving into a highly reactive load, the current could be at nameplate, but the driver throttle is pulled clear back. KW is low, and the alternator current is high. And the stator gets hot.
Then there are a couple of more limiting issues:
- With high lagging loads (inductive) the rotor current is also high. The voltage tends to swag, and the regulator compensates by jacking up the rotor current. This adds significant heat to the stator. So, for lagging loads, the KVA rating is lower than nameplate.
- With high leading loads the voltage tends to climb. The VR reacts by lowering the rotor current. And that reduces the magnetic flux in the rotor/stator air gap. That magnetic field is what transmits the power from the driver shaft (rotor) to the stator. With less magnetic flux, less power can be transferred. So, for leading loads, the KVA rating is lower than nameplate.
- And sometimes, in the leading KVA, low KW quadrant, there will be a small quarter circle cutout. If this one shows up, it is from VR instability. This one is rarely a problem. The generators rarely operate in this area.
All this data will be on a Generator Capability Curve. See the attached sample.
The driver horsepower does not show up on this curve anywhere. The gen manufacturer rates the generator for a specified KW. And they will list all the limitations - ambient, altitude, power factor, duty cycle (prime, continuous, standby). And they will supply a driver that will do that. The driver has to supply the engine auxiliaries, coolers, alternator friction and windage, exciter, power loss to alternator impedance, and other stuff that eludes me. However they tend to not add even one extra mouse power - cause that costs money.
So, if the driver horsepower showed up on a generator spec, I would look for the context. If it were part of the MFG describing an industry standard engine they were buying as part of the spec, I would be okay with that.
But if it were a color glossy ad proclaiming, "We provide a FULL 100hp engine with all our 50KW gens!" I'd be thinking - Ah-ha they hired a Sears ad campaign writer. I wonder what else they are lying about.
Generator Specs - per the worm