That may depend on the "service factor" or whatever equivalent name that internal combustion engines have. If the motor is rated 100 kW and you put additional load on it, will it attempt to drive the additional load or will it immediately stall if loaded to 101kW? I would like to think it can have some overload for at least a short time without much harm. Or do they commonly size the prime movers that close to the alternator capabilities and run them at/near their absolute peak capabilities? I understand that voltage and frequency may not remain all that constant during a surge in load, but if prime mover has the ability to recover it will still ride through instead of stalling.In answer to the original post, the maximum kW output of the generator is determined by the engine. The kVA is determined by the alternator. The engine is limited by its ability to drive a physical load. The alternator is limited by the amount of current it can carry without overheating.
The 100 kW generator has a rated power factor of 80%, which gives the genset a rating of 125 kVA. But if you place a load of 125 kVA at 95% power factor on the engine, it will stall because 125 kVA @ 95% power factor is 119 kW and exceeds the rating of the engine. The alternator can handle it, but the engine can't.
On the other extreme, I once saw what happens when a farmer mis-wires a motor and creates a line to line fault in the process, then tries to run it with his tractor PTO driven 20 KVA generator, but uses a tractor that can deliver 125+ HP to the PTO shaft. Lets just say the tractor did not stall but the generator did.