clyde snyder
New member
- Location
- point pleasant n j
we wired a 60 KW 3 phase Generac generator with 3/0 copper from the generator to the transfer switch ( rated 200 amps), from the meterpan to the transfer switch and from the transfer switch to a 200 amp main breaker 40 circuit panel. The generator came from the factory with a 250 amp 3 pole breaker. The maximum output of the generator is 208 amps. We failed inspection because of the 250 amp circuit breaker. The inspector says we either have to change the conductors between the generator and the transfer switch or change the 250 amp generator circuit breaker. According to the supplied Generac doesn't have a 3 phase 200 amp replacement breaker. I dont understand the logic since the generator's maximum output is 208 amps.