Generator Main Breakers

laketime

Senior Member
Looked at a customer supplied generator yesterday to price for wiring. The customer purchased a 400amp single phase ATS which will be tied into the feed to the residence. The generator has (2) main circuit breakers; (1) 200 amp and (1) 100 amp. The feeders off these breakers will land in the same spot in the ATS like a parrallel feed but from two different circuit breakers. Will this work? Seems to me something is amiss.
 
Work? Maybe, but I think not.
Code compliant? No.
Safe? Doubtful.
Yeah seems to me this generator was supplying two different loads or something. The customer wants me to change to a larger circuit breaker but I do not want to tamper with how the thing is built.
 
Top