The problem here is, with a solidly-connected grounded conductor, the generator is not an SDS. Therefore the grounded conductor is considered part of the service system. It does not matter where the generator OCPD is located. The grounded conductor is not switched or otherwise isolated from the service grounded conductor. Code designates only two types of sources in this regard, a service system and an SDS system. Again, we've already established that with a solidly-connected grounded conductor, the generator is not an SDS.I'd like to work with you on this but generator feeders can only be service conductors if the utility would own the generator and i don't see any reference to allowing 250.24(C) for minimum size in article 225 or 220 if the neutral does not have a load. Maybe somebody can address this.
Rick
This is similar to one trying to size a service or feeder neutral conductor based solely on the calculation of 220.61. Taking that section in the context of its requirements, one could install the smallest neutral conductor for the calculated value. That section does not indicate there is a minimum-size stipulation elsewhere in the code. The same goes for your wanting th size the grounded conductor to the generator, based on the stipulations solely in the feeders section.
If you continue to not see this point on the issue, the best I can do is agree to disagree