Generator & Panel GFI breaker...

Status
Not open for further replies.

1793

Senior Member
Location
Louisville, Kentucky
Occupation
Inspector
I have installed a manual 6 circuit transfer switch at my house and everything seems to work great until I transfer the circuit that is connected to a GFCI breaker in the panel. When switched to Gen. the breaker trips.

The TS has a pre-wired whip with a grounded, neutral, and an EGC. I connected both of these to the neutral bar in the main panel.

What are your thoughts as to why the GFI breaker is tripping and what options are available to fix it?

This GFI breaker feeds my bathroom circuit. I have thought about setting a handy box next to the panel, install a standard breaker to feed a faceless then feed from the load side of the faceless to the bathroom.
 
So it's the GFI breaker in the original panel that's tripping?

Is it because the power is being fed to the circuit through the genny panel, and the neutral is going back through the original GFI breaker? If so, the current on the neutral is what is causing the imbalance and tripping it.
 
So it's the GFI breaker in the original panel that's tripping?

Is it because the power is being fed to the circuit through the genny panel, and the neutral is going back through the original GFI breaker? If so, the current on the neutral is what is causing the imbalance and tripping it.

Yes

That is what I was leaning towards, what about the work-around mentioned in OP?
 
Last edited:
No, my thought was to replace the GFI breaker at the panel with a standard breaker, set a faceless, because of the bathroom requirment, at the panel to feed the circuit.

Gotcha. I misread the part about feeding the load side of the faceless to the bathroom as meaning you already had a faceless in the bathroom.
Your fix would work just fine. Just spend a couple minutes to explain to the customer what you did, and how to reset the GFI (instead of the breaker), That may prevent an unncecessary phone call or service trip.
 
Is it because the power is being fed to the circuit through the genny panel, and the neutral is going back through the original GFI breaker? If so, the current on the neutral is what is causing the imbalance and tripping it.
That is correct. You'd theoretically need a 2-pole switch to overcome this.

That is what I was leaning towards, what about the work-around mentioned in OP?
Won't make a difference. Either both or neither BC conductor must be supplied via the GFCI breaker.
 
No, my thought was to replace the GFI breaker at the panel with a standard breaker, set a faceless, because of the bathroom requirment, at the panel to feed the circuit.
That's a good solution, in my opinion.
 
Why not move the GFI breaker to the TS panel and add your own neutral jumper from the original neutral to the breaker in the new box? Or is this one of those rocker switch panels?
 