I'm wiring a new construction home right now, and the homeowner asked me to price pre-wiring for a backup generator.
I've wired a few, but it's something I only do about once every 5 years or so.
One question relates to 445.13(a)
Must size the conductors at 115% unless the design and operation of the generator prevents overloading
I'm thinking about suggesting a 15kw generator, but maybe 25kw
Thinking about installing a 100-amp emergency panel with built-in ATS from Honeywell
I think it's already full of breakers, none of which are arc fault. Does the listing of this panel specifically include all of those breakers or can they be changed?
If using either 15kw or 25kw, does a 60- or 100-amp disconnect outside constitute overload protection so as to circumvent the 115% requirement?
www.electricgeneratorsdirect.com
I've wired a few, but it's something I only do about once every 5 years or so.
One question relates to 445.13(a)
Must size the conductors at 115% unless the design and operation of the generator prevents overloading
I'm thinking about suggesting a 15kw generator, but maybe 25kw
Thinking about installing a 100-amp emergency panel with built-in ATS from Honeywell
I think it's already full of breakers, none of which are arc fault. Does the listing of this panel specifically include all of those breakers or can they be changed?
If using either 15kw or 25kw, does a 60- or 100-amp disconnect outside constitute overload protection so as to circumvent the 115% requirement?