Customer has small split phase 120/240 generator with 240V L6-30R plug (there are also 120v plugs). He's asking if he can derive 120V from the L6 plug. In essence use a hot and the EGC prong to get 120. I've told them this is a bad idea and probably against code. It's similar to stealing the EGC at regular outlet for a neutral.
I don't have a wealth of generator experience, so I'm asking here to see if there are any alternatives to my thinking and/or code references. Realistically what he's asking would work, and the cable that plugged into the L6 outlet would act like service conductors where the neutral/grounded conductor is accomplishing both the neutral and EGC, but I didn't think this was permissible. Perhaps they (neutral and egc) could then be split at small panel next to the generator.
Generator states the neutral is bonded to the frame.
I'm not actually sure why they are wanting to do this in the first place, but that's a different question...
Thanks in advance
I don't have a wealth of generator experience, so I'm asking here to see if there are any alternatives to my thinking and/or code references. Realistically what he's asking would work, and the cable that plugged into the L6 outlet would act like service conductors where the neutral/grounded conductor is accomplishing both the neutral and EGC, but I didn't think this was permissible. Perhaps they (neutral and egc) could then be split at small panel next to the generator.
Generator states the neutral is bonded to the frame.
I'm not actually sure why they are wanting to do this in the first place, but that's a different question...