We have several generators on campus that each feed emergency power only in 2-3 buildings at a time. I consider these multiple generator power circuits to fall under Article 225 Outside Branch Circuits and Feeders, and specifically art 225.30 (A). I also point to 225.32 Exception #1 for locating disconnecting means for the generator power circuit inside each building. I was told by another engineer that these generator circuits feeding multiple buildings are actually services and need to be installed per 230.6 and 230.70. I disagree with him and am looking for confirmation and perhaps something more specific in the code stating that the generator power feeders routing to multiple buildings are not services but outside branch circuit feeders. Please let me know what your interpretation of the code is for generator power feeders.