I recently quite my job that Ive had for 12 years to work with Doctors without Borders. My new job is energy manager at a hospital in Sierra Leone. Its kinda fun and kinda sucks at the same time.
We do have a very modern energy plant. We run on three 220 KVA synced Cat gensets. There is no utility connection. Currently we run on only one generator and our load is around 55 KVA. So its a fraction of one generator.
The problem we have been having is when we switch on 10 mini split HVAC units. All the units have small inverters. This causes -kvar back onto the generator. The generator sees -kvars of 5 - 10%. This caused the generator to shut down on alarm.
Another 50kVA generator was provided to supply just the 10 AC’s, but during commissioning with this 50kVA it shutdown a number of times due to Over Voltage. A Fluke power analyser was used to assess the power quality during the commissioning and we observed a high Lagging Power factor on at least one phase.
We contacted the CAT and they said to set the shut down to 20% -kvar on the 220 KVA gensets. Since then we have been able to run fine.
The problem is we will be bringing a lot more air conditioners online. We are worried this will increase the -kvar and put us into shut down again.
The problem is negative reactive power generated by the mini split HVAC units. I think this is causing distortion power factor. My solution to this would be line reactors. The electrical foreman running the construction thinks we should put in a power factor correction capacitor bank.
Its my first week at the hospital so I dont have a lot of data or experience to go on.
Whats the best solution to this problem?
We do have a very modern energy plant. We run on three 220 KVA synced Cat gensets. There is no utility connection. Currently we run on only one generator and our load is around 55 KVA. So its a fraction of one generator.
The problem we have been having is when we switch on 10 mini split HVAC units. All the units have small inverters. This causes -kvar back onto the generator. The generator sees -kvars of 5 - 10%. This caused the generator to shut down on alarm.
Another 50kVA generator was provided to supply just the 10 AC’s, but during commissioning with this 50kVA it shutdown a number of times due to Over Voltage. A Fluke power analyser was used to assess the power quality during the commissioning and we observed a high Lagging Power factor on at least one phase.
We contacted the CAT and they said to set the shut down to 20% -kvar on the 220 KVA gensets. Since then we have been able to run fine.
The problem is we will be bringing a lot more air conditioners online. We are worried this will increase the -kvar and put us into shut down again.
The problem is negative reactive power generated by the mini split HVAC units. I think this is causing distortion power factor. My solution to this would be line reactors. The electrical foreman running the construction thinks we should put in a power factor correction capacitor bank.
Its my first week at the hospital so I dont have a lot of data or experience to go on.
Whats the best solution to this problem?