I'm getting a foggy picture of your comment.
I was of the impression augie was talking about putting a DT disonnect ahead of the [original?] service disconnect. The DT switch is the transfer switch... and due to its placement would be required to be service equipment rated. If there is no ocpd associated with the DT switch, as in integral or located immediately adjacent thereto, it would not be the service disconnect and thus relocation of the earth bonding would not be required. At this point I'm not even certain such would be compliant, but cannot think of any prohibition offhand. Regardless, I would never suggest such an installation. My preference is to just replace the service disconnect with a service-entrance-rated transfer switch, or a non-service-entrance-rated one somewhere "downstream".