None that I've heard of.
Generally you pick a kW size, check with the manufacturers that you are going to permit to bid, get the footprint for the largest of those possibilities, consider space needed for start batteries, battery charger, fuel day tank, silencer, freestanding output breaker if needed, and approx 4' clearance around for maintenance (more if you can get it). Also make sure that you can get it in the room you are considering thinking of size and weight.
I just laid out (4) 2500kW's and Detroit got the project (providing 2800kW's). Luckily, we used Detroit for the lay-out, because they were the biggest footprint in that size frame.