My understanding has been that moulded case breakers should be rated using the subtransient fault current.looks like euro data sheets give much more info
direct and quadrature axis values
sub and transient valued
http://www.kohlerpower.com.sg/onlinecatalog/pdf/KX2200C.pdf
how are breakers rated?
transient, sub, sym steady-state???
is the subtransient value factored into the rating?
is the tc so short as to not be a factor? I^2 t ? ~ 1 cycle
with a genset that seems to be the caseMy understanding has been that moulded case breakers should be rated using the subtransient fault current.
That does not make sense.good read
http://www.apt-power.com/wp-content/uploads/Generator_X_to_R_ratio1.pdf
so if X'd <= sqrt3 x X"d
isc = V/X'd > V/(sqrt3 x X"d)
The OP has the generator data.with a genset that seems to be the case
obtaining the direct quadrature value from the util might be hard
I guess you could calc/est a number based on system x/r
isc = S/(sqrt3 v puZ) is a sym value which is typically used for sizing
xfmr L will dampen the subtransient I guess
we only know he has X'dThe OP has the generator data.
That does not make sense.
Source for X'd is same as X''d so should be available.we only know he has X'd
Not clear.that could be interpreted 2 ways
I was not clear
you do not understand
from link
isc" = V(sqrt3 X"d)
isc' = V/X'd
let
V = 1 pu
X"d = 0.10 pu
X'd = 0.17 pu
isc" = 5.77 V pu
isc' = 5.88 V pu
moot
some texts say mult isc" x 1.5 (1.6) to account for the dc component
and 1.2 for isc'
assumptionSource for X'd is same as X''d so should be available.
Not clear.
Where is your link stating E/X'd? Where is it using a different voltage?
The DC component should be higher at isc'' because it will have less asymmetric decay than isc' (which is taken to be later in the fault). A conservative value to size equipment is to use 2X for the DC offset at isc''.