i have a customer that wants to size a generator for this epuipment. They cant get [permanent power at this time so this is best option for them per them. I am trying to help them determine the size of generator needed. The FLA is based on Table 430.250 All 3 phase 480 I am not sure how to add the 120v loads. If you guys dont mind I need a hand. They do mention PF is 70% but Im not sure where they are getting that number.and first 5 motors do have VFDs
1. 200hp 240a x 125%= 300a Largest Motor add all remaining flc
2. 200hp 240a
2a. 100hp 124a
3. 90hp 124a
4.90hp 124a
5. 50hp 65a
6. 50hp 65a
7. 40hp 52a
8. 20hp 27a
9.20hp 27a
10. 20hp 27a
11. 3hp 4.8a
total 1179 amps
not to mention
1. 2.3 hp 120v 24a
2. 5.6 hp 120v 56a
3. 5.6 hp 120v 56a
4. 5.6 hp 120v 56a
would this be added to the load at the end? they will need xfmr for 120v but just trying to figure size generator.