dlamp67 said:
... We have been told ... Any input??
By whom and citing what ???
A few comments:
1) The ATS isn't required to be "service rated"
if there is a service-rated disconnect between the meter and the ATS (the "disconnect" actually becomes THE service)
IMO this is also a better design as it allows you to easily and
completely deenergize the ATS enclosure for maintenance and/or repair.
2) The ATS does need to be rated to carry the full service -- or service disconnet- current (i.e. 400 in this case) as the ATS is "inline" between the service and the loads.
3) As far as arbitrarily sizing an "
optional" genset (see Art 702 definition) to carry the "full 400" ... that's just silly. (although I'm not doubting that's what you were told)
How much of that "400" is the customer actually even using?
If a customer wants only enough
optional backup power to run a single light bulb, that his perogative (702.5).
4) Lastly, a too-lightly-loaded genset (i.e. oversized) is not a "happy genset" -- all sorts of mechanical problems (mostly prime-mover related) can arise from long-term light-loading
Hopefully the Mike Holt drawing below will help illustrate the electrical points: