Generator size

Status
Not open for further replies.

dale87

New member
Location
illinois
*customer needs to run 2 motors*
*1. 60 hp 120/240 3 phase .85 PF 93%eff. @141 amps 60hz
*2. 20 hp *120/240 3 phase .85 pf 93%eff @48 amps 60hz

*the 60 will start first then the 20. what size 120/240 3 phase generator in KW
 

bob

Senior Member
Location
Alabama
Dale
If you google "sizing electric generator design software" you will find a number of sites
that will allow you to download a program that will size the generator for you.
Caterpillar has a nice one.
 

iceworm

Curmudgeon still using printed IEEE Color Books
Location
North of the 65 parallel
Occupation
EE (Field - as little design as possible)
*customer needs to run 2 motors*
*1. 60 hp 120/240 3 phase .85 PF 93%eff. @141 amps 60hz
*2. 20 hp *120/240 3 phase .85 pf 93%eff @48 amps 60hz

*the 60 will start first then the 20. what size 120/240 3 phase generator in KW

Curiosity Question: (nothing to do with sizing your generator)
I've never seen a motor with a "120/240 3phase" nameplate rating. What brand and how old is it?

ice
 

bob

Senior Member
Location
Alabama
Dale
I used the Generac Software and it recommended 175 kw. WSuggest you talk to a mfg.
Let us know what you find.
 