the load supplied is all that really matters. Your mentioned items though on 8 different branch circuits are the type of load that doesn't draw much and is possible they could be all on just one maybe two branch circuits. If that is the case a 20 or 30 amp feeder is sufficient to handle them and so would be a generator with only 20 or 30 amp output capacity.So then it is OK to install a 100A MB in the existing 208/120V panel and feed the ATS.
Use A 20KW 208/120 3p generator, install a 208/120v 3ph panel off the ATS and put the 8 120v loads in that panel.
I was concerned that taking 100A to the ATS would be too much. It would be equal to the MBR of the existing 100A 3P 120/208v panel.
At same time even if you fed this with a 200 amp conductor it still only draws less than 30 amps and a 30 amp generator would still have no problem with supplying it.
Lets say your panel supplied by a 100 amp feeder only had a total connected load of 58 amps. A generator capable of delivering 58 amps is really all that is needed even if you still ran 100 amp conductors to it. It won't deliver any more than what is demanded by the connected loads and overcurrent protection will keep it from being overloaded should something happen where it does try to deliver more than it is rated for.