Generator sizing, electronic loads, and load bank.

Status
Not open for further replies.

Fulthrotl

~Autocorrect is My Worst Enema.~
The A/C will act as a load bank if it will run year round. The load bank would be if it were a diesel and you needed it to load past 50% load, avoiding wet stacking.

yeah, what he said.:D

i've only seen load banks used in the 1 megawatt range, on a data center i
did, and the load bank was only used to load the generator when it was ran
once a week, so it wouldn't run under no load, and get gummy.

load bank on a little one...? when i was breaking in my little honda 2kw
portable, i plugged in a hair dryer.... a 1500 watt load bank.... :smile:
 

JES2727

Senior Member
Location
NJ
The generator controls are confused by the electronic loads and keep trying to change the frequency and voltage to what the generator output is supposed to be, but is always a step behind the load and the voltage and frequency output from the generator is not steady.

Thanks for the explanation Don. Makes perfect sense....
 