O olc Senior Member Apr 22, 2019 #1 Standby generator sized for a whole building (100KW ball park - gas fired): With a 120/240V 3 phase service given that there is probably a significant larger load on the two poles (for lighting etc.) - How does that affect the generator sizing?
Standby generator sized for a whole building (100KW ball park - gas fired): With a 120/240V 3 phase service given that there is probably a significant larger load on the two poles (for lighting etc.) - How does that affect the generator sizing?
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Apr 22, 2019 #2 In several ways. 1. You have to make sure the generator can be wired 3ph 4-wire like your service. 2. You have to presume all phases will see the load level your greatest loading is.
In several ways. 1. You have to make sure the generator can be wired 3ph 4-wire like your service. 2. You have to presume all phases will see the load level your greatest loading is.