If the inverter is converting 74VDC to 120VAC, then you must have a 74VDC supply. That means a battery charger. Do you have data on the AC-to-DC converter?
Solid state battery chargers are noted for high harmonic draw. Ferroresonant are much better. However, you need to hold the THD on the voltage low enough for the charger to work. That means oversizing the generator by a factor of 3-5x. So, for 5kW of load, a 25kW generator may be needed.
However, too many unknowns. If the generator is one using inverter technology, it might be more tolerant than a traditional wound generator.