So use a myers hub on the top conduit OR run the feeders to the TS via the same lower nipple as Augie had suggested above.

I drew 2 conduit nipple to keep the diameter smaller but now that I look at it again using a single larger conduit on the bottom should be feasible.

I’m very doubtful this will ever see weather, as there’s a 6’ eave overhead. But I get it compliance is compliance.
Or a sealing locknut.
 
The full-sized neutral does not need to enter and leave the ATS; the load neutral only needs to land on the service breaker's neutral bus. A single neutral sized for the generator is all that is needed between the service neutral and the ATS neutral.
Thanks.

Would save a splice doing it this way, since load neutral is already going to the service neutral bus. Would just run a 2awg from the service neutral bus to the TS neutral bus.

 