I know a lot of smart people visit this site so I'm gonna pitch this one out there hoping to solicite some help...
Some history -
I am working on a power upgrade for a communication facility which has been piece mealed by God only knows who over the years which involves replacing an 800A generator ATS ( existing mounted outdoors in a NEMA 1 enclosure with extensive water damage ) as well as adding a new 800A main distribution panel. We are also replacing two small -48 vdc power plants with a 1000A plant. There are two 200KW diesel gensets to provide emergency power that are connected in a redundant configuration, not connected in parallel, as well as a 60KVA three phase UPS system for the AC loads.
This has to be accomplished with zero downtime.
To the present -
We tested and had to replace the UPS battery string prior to the transition-
We have replaced the DC plant and swung all DC loads - 500 amps worth without any issues and have decommissioned the old plants.
Replaced the damaged generator ATS, reconfig'd both generator ATS's to operate in a redundant fashion, & installed the new main distribution panel.
Now my issue -
During the transition we had to run on generator power for approx. 30 hours.
I noticed during the transition that on one genset (the newer one - an Onan diesel) that every time an air handler came online the UPS would cycle to battery. The HVAC units are not on the UPS but are connected to the generator. This only occurs with the newer Onan genset. The old Onan genset ( around 15 years ) it doesn't occur. Both generators have electronic govenors and are not undersized for the loads and should have no issues with the inrush of the HVAC compressors.
I connected a Fluke 43B during the transition and didn't see any abnomalies
(I don't have a 3P PQA)
We increased the generator output frequency to 60.1-61.0 Hz and noticed the problem seemed to decrease but the power factor went to *&^%
The generator maintenance company checked the generator and found no problem. I spoke with the UPS company FE who said we should all meet, put facility load on the system and make some adjustments ( coordination ) between systems.
Any suggestions / similar experience would be appreciated.
I know a lot of smart people visit this site so I'm gonna pitch this one out there hoping to solicite some help...
Some history -
I am working on a power upgrade for a communication facility which has been piece mealed by God only knows who over the years which involves replacing an 800A generator ATS ( existing mounted outdoors in a NEMA 1 enclosure with extensive water damage ) as well as adding a new 800A main distribution panel. We are also replacing two small -48 vdc power plants with a 1000A plant. There are two 200KW diesel gensets to provide emergency power that are connected in a redundant configuration, not connected in parallel, as well as a 60KVA three phase UPS system for the AC loads.
This has to be accomplished with zero downtime.
To the present -
We tested and had to replace the UPS battery string prior to the transition-
We have replaced the DC plant and swung all DC loads - 500 amps worth without any issues and have decommissioned the old plants.
Replaced the damaged generator ATS, reconfig'd both generator ATS's to operate in a redundant fashion, & installed the new main distribution panel.
Now my issue -
During the transition we had to run on generator power for approx. 30 hours.
I noticed during the transition that on one genset (the newer one - an Onan diesel) that every time an air handler came online the UPS would cycle to battery. The HVAC units are not on the UPS but are connected to the generator. This only occurs with the newer Onan genset. The old Onan genset ( around 15 years ) it doesn't occur. Both generators have electronic govenors and are not undersized for the loads and should have no issues with the inrush of the HVAC compressors.
I connected a Fluke 43B during the transition and didn't see any abnomalies
(I don't have a 3P PQA)
We increased the generator output frequency to 60.1-61.0 Hz and noticed the problem seemed to decrease but the power factor went to *&^%
The generator maintenance company checked the generator and found no problem. I spoke with the UPS company FE who said we should all meet, put facility load on the system and make some adjustments ( coordination ) between systems.
Any suggestions / similar experience would be appreciated.