We had a power outage at our plant this weekend, and like ususal went to fire up our generator. For some reason however we had problems with the generator and were not able to bring it online right away. The generator is a 480V generator.
The first issue that we had was that the breaker on the generator was tripped, and therfore power was not supplied to our system right away. I am not sure why this breaker was tripped. When we reset the breaker it kept tripping and we could not figure out why. Finally we took some volatge readings off of the generator and found the output voltage to be only 314V. After seeing this one of the electricians turned a dial on the side of the generator which increased the voltage to 385V, and finally the breaker stopped tripping. This 385V lead to voltage problems with other equipment in the plant however we were never able to get the volatge any higher.
What would cause this voltage to be such a low value? I'm assuming that this low voltage was what was tripping the breaker maybe on an UV trip however I'm not sure. I'm not familiar with generators so I'm not sure what the knob on the the side was for or why it increased to voltgge when adjusted. Does increasing the rpms of the generator have anything to do with the voltage or is this something else?
I have a tecnician coming to look at the generator however I was hoping to get some explanations of theoretical answers from you wonderful people.