Finally had a chance to look over these code references, 702.11 does not require it to be service rated, it only requires that it be readily accessible and within sight of the building or structure supplied. which the generator install picture complies with. The one part of article 702 that this install did not comply with is 702.8, Inspector must have missed that one.
After reading article 225, I do not think it is the intent of this article to include generators, as in 225.2 does not include any articles on generators. Also the wording in the scope is ....for the SUPPLY of utilization equipment.... It is a good practice to have a disconnect next to the service because it makes it easy on the firefighters to kill building power, but when installing large generators, it is not practical. I knew there was a reason I mentioned Mecklinberg county NC, in a previous post, I remember know that it was the only jurisdiction that required a main before going into the building, the key switch was not acceptable to there code compliance department. The toughest one I ever did was Beaver Creek Ohio, and they did not require it.