Power Service:
Utility: 120/240VAC/3PH/60Hz/200AMP Open Delta
Generator: 80KW
We need the 80KW because we can't have higher than 10% voltage dip.
The 200AMP utility Service feeds a 200Amp Main Breaker which feeds a 400AMP rated Automatic Transfer Switch (ATS) which feeds a 200AMP rated panelboard (PB)which has a 200AMP Main Breaker.
The 80KW generator comes with a 250AMP breaker. Hence the need for the 400AMP rated ATS.
Would an electrical inspector have "Heartburn" about the generator having a higher AMP capacity than the panelboard?
Since we are actually only using 50% of the generators KVA capactity, is there anything wrong with lowering the generator's breaker to 200AMPs.
and using a 200AMP ATS?