Re: generators 4 poles switching
Chuck,
As Dereck has stated, without GFP installed at the service, the generator system can be SDS or non-SDS.
The determining factor is often the internal connections of the generator, specifically, whether the winding center-tap (neutral) is bonded to the frame or not.
Because small portable "stand-alone" generators are required to have the neutral-frame bond connection when used with cord-connected loads, the trouble arises when someone connects one of these, through a transfer switch, to a facility system, without switching the neutral, or removing the neutral-frame bond connection.
Ed
Chuck,
As Dereck has stated, without GFP installed at the service, the generator system can be SDS or non-SDS.
The determining factor is often the internal connections of the generator, specifically, whether the winding center-tap (neutral) is bonded to the frame or not.
Because small portable "stand-alone" generators are required to have the neutral-frame bond connection when used with cord-connected loads, the trouble arises when someone connects one of these, through a transfer switch, to a facility system, without switching the neutral, or removing the neutral-frame bond connection.