2. Up in the hills, I have a 12k generator accompanying the solar system for a house. The neutral is bonded to the frame of the generator. I am going to install a disconnect for the generator, and make the hookups, a first for me.
I am not sure how the solar installer wired the ATS, and am not sure if it switches the neutral yet. In this case, I'm not convinced it matters.
Here's the thing: Since the generator is to energize the 120/240 panel in the house, and also to charge the batteries via the inverters (which would be the 'other' supply for the house) I kind of assume the ATS isn't conventional at all. The operation of the system makes it sound more like a disconnect than a transfer switch.
My question: in this circumstance, where the supplies are intentionally to be tied together, do I need to concern myself with traditional grounding methods? Generally, if the generator is bonded neutral to ground, then the neutral must be switched in the ATS. Is there an opportunity for objectionable current if the neutral is not switched? It seems more like an extension of the same system in this case.
If I had my druthers, the neutral/grounding bond would take place in the proximity of the inverter/battery room, and I would just remove the bond at the generator (if I could find it). Whether the neutral is switched or not seems unimportant in this case.
Given the high-tech nature of the equipment involved, I doubt I can just tone through and see if the ATS switches the neutral. With the inverters, the ATS, controllers, etc, there's more LCD's and LED's than Radio Shack. I'm probably going to get ahold of the solar installer and determine the switch operation from him.
I'm probably overthinking this. (That whole well pump thing: Yeah, somebody else is taking care of it.
)
2. Up in the hills, I have a 12k generator accompanying the solar system for a house. The neutral is bonded to the frame of the generator. I am going to install a disconnect for the generator, and make the hookups, a first for me.
I am not sure how the solar installer wired the ATS, and am not sure if it switches the neutral yet. In this case, I'm not convinced it matters.
Here's the thing: Since the generator is to energize the 120/240 panel in the house, and also to charge the batteries via the inverters (which would be the 'other' supply for the house) I kind of assume the ATS isn't conventional at all. The operation of the system makes it sound more like a disconnect than a transfer switch.
My question: in this circumstance, where the supplies are intentionally to be tied together, do I need to concern myself with traditional grounding methods? Generally, if the generator is bonded neutral to ground, then the neutral must be switched in the ATS. Is there an opportunity for objectionable current if the neutral is not switched? It seems more like an extension of the same system in this case.
If I had my druthers, the neutral/grounding bond would take place in the proximity of the inverter/battery room, and I would just remove the bond at the generator (if I could find it). Whether the neutral is switched or not seems unimportant in this case.
Given the high-tech nature of the equipment involved, I doubt I can just tone through and see if the ATS switches the neutral. With the inverters, the ATS, controllers, etc, there's more LCD's and LED's than Radio Shack. I'm probably going to get ahold of the solar installer and determine the switch operation from him.
I'm probably overthinking this. (That whole well pump thing: Yeah, somebody else is taking care of it.