Generators running a machine shop?

fastline

Senior Member
Location
midwest usa
Occupation
Engineer
I work in this space so I got tasked or rather asked about this. The reason I'm here asking is I want to hear any possible concerns or downsides here such as frequency regulation, regenerative drive backfeed, etc. Really anything that could possibly be a concern.

For info, most machines with any HP over 10 would be VFD but if you guys don't know CNC land, we accelerate FAST! Less than 1sec and constantly. I can't say I would know how to exactly size a generator to ensure solid operation, but also knowing that oversizing, especially with diesel is a big no-no.

But on that subject, I don't know if diesel or LP would give better frequency regulation? Hopefully enough mass to grunt through?

And for sizing, probably 2-3 machines for now with est very full load of 75kw. So probably targeting a 60-100kw generator. Keep in mind these machines can reduce loads and the goal was set to sort of see how much can be run, and consider upgrading to bigger later.
 
Since generators typically present a higher source impedance than a POCO supply of similar kVA capability, nonlinear load currents may develop relatively higher harmonic voltages when on a generator. Delta-wye drive isolation transformers on VFDs, for example, could help block harmonic currents if there are other loads that are sensitive to voltage harmonics.
 
Is this in a place completely devoid of any power, or do you just not have a 3-phase service? If you have a fairly decently sized single phase service, you could also look into perhaps utilizing rotary phase converters? North American Phase Converter makes a 100 Amp model, and American Rotary has a similar offering. You could either do individual smaller units for each machine, or try to go large and cover multiple units with a single converter. They claim these are pretty good for CNC.


 
The generator manufacturers provide sizing software that allows you to evaluate all kinds of motor loads like ATL, Y-Δ, 6-pulse or 12-pulse CT/VT VFDs. I have used the Cummins one for years, but there's also MTU, Rehlko and Generac. Your local sales rep will hook you up or even run it for you.
 