Customer with a Gen set with nameplate of 346 amp @ 240v. Single phase. It will be mounted in an enclosed trailer used at job sights. to power their equipment that is also mounted in the trailer. Art 445.13 of the '14 NEC Indicates the conductors shall not be smaller than 115% of the nameplate current rating to the first distribution device(s). Parallel 3/0 cu in two conduits should do it but I was hoping to split that into two 200 amp CB or fused Discs to supply one large load, and a load center. I read it as I need 400 amp conductors to each disconnect. No taps. Is that correct?
The gen set is labelled as standby but will not be used in that sense.