S sleepy Senior Member Jan 14, 2005 #1 my question is with generators in health care facilities, in the nec i was told that you have to have a on site fuel source, does that mean you cannot have natural gas?
my question is with generators in health care facilities, in the nec i was told that you have to have a on site fuel source, does that mean you cannot have natural gas?
iwire Moderator Staff member Location Massachusetts Jan 14, 2005 #2 Re: generators Maybe yes, maybe no. Look at Section 700.12(B) and the exception. Basically it is up to the AHJ.
Re: generators Maybe yes, maybe no. Look at Section 700.12(B) and the exception. Basically it is up to the AHJ.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Jan 14, 2005 #3 Re: generators Be careful here, there are a lot more documents than just the NEC that govern health care facilities. Don
Re: generators Be careful here, there are a lot more documents than just the NEC that govern health care facilities. Don