hurk27
Senior Member
- Location
- Portage, Indiana NEC: 2008
I agree with that.
If you were to apply that though then each of the two gen sets would be none seperately derived systems because they are each tied to another system.
The definition of SDS does not change the wording in 250.20(D). If the wording had said "or to another alternate source", then things would be a little clearer.
Rick
So either the definition in artical 100 is flawed, or the FPN in 250.20(D) is?
because if the generators are not a SDS as defined in artical 100, 250.20(D) would not apply?