I need some help
I was checking out an older 45 KW generator that is set up for 480Y/277 output.
When I measure the output I find about 50 volts (no load) and this could actually be phantom voltage.
The generator control panel has a breaker labeled 'exciter circuit'.
If I flip it off than on again my meter shows 450 volts on the output for a moment than drops back to 50 volts.
The 'exciter circuit' breaker is not opening after I flip it on I checked that a few ways.
If it helps this is an Onan generator at least 25? years old.
Glad to hear any suggestions (except higher an electrician
) and if anyone has recommendations for some generator repair / theory books I would be glad to hear them.
Thanks, Bob
I was checking out an older 45 KW generator that is set up for 480Y/277 output.
When I measure the output I find about 50 volts (no load) and this could actually be phantom voltage.
The generator control panel has a breaker labeled 'exciter circuit'.
If I flip it off than on again my meter shows 450 volts on the output for a moment than drops back to 50 volts.
The 'exciter circuit' breaker is not opening after I flip it on I checked that a few ways.
If it helps this is an Onan generator at least 25? years old.
Glad to hear any suggestions (except higher an electrician
Thanks, Bob