I need some help
 
I was checking out an older 45 KW generator that is set up for 480Y/277 output.
 
When I measure the output I find about 50 volts (no load) and this could actually be phantom voltage.
 
The generator control panel has a breaker labeled 'exciter circuit'.
 
If I flip it off than on again my meter shows 450 volts on the output for a moment than drops back to 50 volts.
 
The 'exciter circuit' breaker is not opening after I flip it on I checked that a few ways.
 
If it helps this is an Onan generator at least 25? years old.
 
Glad to hear any suggestions (except higher an electrician ) and if anyone has recommendations for some generator repair / theory books I would be glad to hear them.
) and if anyone has recommendations for some generator repair / theory books I would be glad to hear them.
 
Thanks, Bob
	
		
			
		
		
	
				