Are you seeing a 1200A medium voltage circuit breaker and thinking the generator should put out that much? 1200A is the smallest MV metalclad breaker available, so the generator will likely put out much less.

A 2,000,000W generator typically has a 0.8pf relationship with the alternator, so it is likely rated at 2MW/0.8 = 2.5MVA. If you calculate Amperage from that at 4160V you will get 347A (at 0.8pf) maximum.
 