Our moderator George has many proposals most he didn't win on. One interesting one is in 310, its very long, and the CMP said, well, we will take a look at it....
Our moderator George has many proposals most he didn't win on. One interesting one is in 310, its very long, and the CMP said, well, we will take a look at it....
If you go here and go to "ROP Ballot" you can read or download all of the proposals and the "unofficial" action taken at the panel meetings. There is a file for each of the code making panels.
are you going to post or link the proposal so we can take a look?
This makes sense except that many times there are a whole bunch of control conductors that have very little current flowing through them and thus generate no heat. There is no need to derate them.All ungrounded conductors capable of being energized simultaneously shall be
considered current-carrying.
This makes sense except that many times there are a whole bunch of control conductors that have very little current flowing through them and thus generate no heat. There is no need to derate them.All ungrounded conductors capable of being energized simultaneously shall be
considered current-carrying.
Maybe it could be rewritten so that it refers to the branch circuits involved. I.e. - you only have to derate for each OCPD.
even multi-wire circuit could have all conductors energized at the same time, of course what is his definition of energized, is it meaning that current is flowing?
This makes sense except that many times there are a whole bunch of control conductors that have very little current flowing through them and thus generate no heat. There is no need to derate them.Control conductors would not be counted as current carrying conductors for the purpose of derating.That is already covered in the code rule.
310.15(B)(3)(a) ... Where conductors of different systems, as provided in 300.3, are installed in a common raceway or cable, the adjustment factors shown in Table 310.15(B)(3)(a) shall apply only to the number of power and lighting conductors (Articles 210, 215, 220, and 230).
That would be a good code change as the use of multiple conductors on a single OCPD will always produce less heat in the cable or raceway than if a single conductor carried the full load.Maybe it could be rewritten so that it refers to the branch circuits involved. I.e. - you only have to derate for each OCPD.
Our moderator George has many proposals most he didn't win on. One interesting one is in 310, its very long, and the CMP said, well, we will take a look at it....
I shall accept the title of "Prominent Loser" with all due humility.
Here is the ROP for panel #6
and he was right it is long, scroll down to the PDF page 13 to 17
George are ya trying to keep them from ever getting it done on time or what :lol:
This makes sense except that many times there are a whole bunch of control conductors that have very little current flowing through them and thus generate no heat. There is no need to derate them.
Control conductors would not be counted as current carrying conductors for the purpose of derating.
That would be a good code change as the use of multiple conductors on a single OCPD will always produce less heat in the cable or raceway than if a single conductor carried the full load.
There is a similar rule for wireways that control conductors do not have to be derated if under 10% of ampacity