john37
Senior Member
- Location
- Riverside, California
I have a project where I'm trying to determine where to get power for a new small guard structure that is being built at the entry of the property. The service will be at 480V, 1ph because the length of the run is about 600 feet. I need about 30 amps to for the small guard structure to supply power for lights, receptacles, and a/c. I'll provide a step down transformer inside the small guard structure.
There is an existing handhole that feeds power to a pump station 480/277V 3ph panel that is located across the road where the new guard structure will be located. Per code, is it allowable to tap the existing feeder inside the handhole to extend a new feeder to the guard structure if the existing feeder has spare capacity? It's a 200 amp feeder and the existing pump station is currently drawing 30 amps at 480V.
We are trying to avoid trenching across the road where the pump station 480/277V panel is located. Thank you.
There is an existing handhole that feeds power to a pump station 480/277V 3ph panel that is located across the road where the new guard structure will be located. Per code, is it allowable to tap the existing feeder inside the handhole to extend a new feeder to the guard structure if the existing feeder has spare capacity? It's a 200 amp feeder and the existing pump station is currently drawing 30 amps at 480V.
We are trying to avoid trenching across the road where the pump station 480/277V panel is located. Thank you.