paul
- Snohomish, WA
I would make a long distance phone call to the landlord and tell them to make a local phone call to a local electrician who can go out and troubleshoot the issue.
So what is the safeguard inbuilt in NEC against shock such as mentioned in the OP for a lost service neutral?
Proper bonding & grounding will help for the most part.
We really need to know what two points the victims got shocked between to go much further.![]()
Looking for the proactive NEC Art No......., Where is it?!Don't touch metal parts when the service neutral is open. That is the safeguard.
I do not see how grounding will really do anything.
But nothing "shocking" about the panel!![]()
So making a equipotential ground plane around any outdoor metal pole not required; just bond the EGC with the pole; that is all required, correct?
[FONT=Georgia, Times, Times New Roman, serif]As noted in 110.7 of the 2011 NEC, "completed wiring installations shall be free from short circuits, ground faults, or any connections to ground other than as required or permitted elsewhere in the Code.", but it does not talk about what to do in advance for a broken POCO neutral outside but very near the building premises. That is what is called pro-activity.[/FONT]110.7
Sure.Try to stay on the topic.
I already suggested to use ground fault protector in the main supply-a proactive approach. But it not even vetted here.The NEC has nothing to do with the power company neutral.
If you have a solution to this please send in a change proposal to the NFPA.
I already suggested to use ground fault protector in the main supply-a proactive approach. But it not even vetted here.![]()