I'm installing a 40kw 10k solar array that is going to, when combined output 120/208 3phase, on a building we intend to connect to the 277/480v service. There are no existing transformers close to where I need to convert to the 277/480 that I am able to tie into, so I need to supply a transformer.
I was given the transformer "everybody uses for this" and am concerned about connecting it up.
The transformer is a 480v delta primary with a 120/208 wye secondary. Originally I thought this was perfect until I read that I cannot connect the x0 point on the transformer if using it to backfeed, which I am.
the 10k solar inverters do not actually output a neutral, they do not establish a ground point on the inverters like the old enphase microinverters, however it would seem I still need one as when connected in the 3 phase system it won't be balanced perfectly. They output 208 single phase on one inverter, I have 6 inverters that I will be connecting to a 3 phase combiner panel that will then produce a 208 3 phase system.
I am wondering if, because there is no other reference to ground on the secondary side of the transformer, if applying a GEC to the x0 and creating a grounded conductor reference at that point, if that should be OK, of if I need to find another solution. Is it possible they are actually producing 208 delta and I don't need to connect a neutral at all to the system?
any thoughts would be greatly appreciated.
I was given the transformer "everybody uses for this" and am concerned about connecting it up.
The transformer is a 480v delta primary with a 120/208 wye secondary. Originally I thought this was perfect until I read that I cannot connect the x0 point on the transformer if using it to backfeed, which I am.
the 10k solar inverters do not actually output a neutral, they do not establish a ground point on the inverters like the old enphase microinverters, however it would seem I still need one as when connected in the 3 phase system it won't be balanced perfectly. They output 208 single phase on one inverter, I have 6 inverters that I will be connecting to a 3 phase combiner panel that will then produce a 208 3 phase system.
I am wondering if, because there is no other reference to ground on the secondary side of the transformer, if applying a GEC to the x0 and creating a grounded conductor reference at that point, if that should be OK, of if I need to find another solution. Is it possible they are actually producing 208 delta and I don't need to connect a neutral at all to the system?
any thoughts would be greatly appreciated.