- AZ
- Occupation
- Part Time Electrician (semi retired, old) - EE retired.
i dont say this too often, its just one of those things i keep to myself, very obvious that many on this forum, including some mods, dont really understand electricity all that well.
here's an experiment showing you a possible scenario that a 2-wire GFCI will not protect you, and you are possibly dead.
the cord is a non-polarized nema 1- (i polarized it with silver marker). the hot has an inline ~18k resistor. the end of the cord has eyelets soldered on to attempt to mimic real terminations of an appliance. the sink is all plastic so no amps can flow out to a EGC, the water is warm tap water (my water is heavy in minerals and filtered via a water softener, more on this at the end). from the data, the "short" in the water (w/o the inline ohms) would not trip a 15 or 20A OCPD and the GFCI is as happy as a virgin for the 1st time. the stray amps across the unattached amp probes in random location in the water indicates that amps will still flow from wire --> across water --> into the body --> through body --> back into water, and return back to wire !! so as much as some of you think amps only take path of least resistance (WRONG), it takes all paths.
i dont care to explain this elementary experiment, so you'll need to understand it for yourself. in this experiment the amps through the unattached probes would not have been enough to kill, but the scenario shows the possibility exists.
voltage across end of wire no-load
short circuit amps
wires ends in water
amps of wire in water
amps probes just in water, not attached to anything
amps flowing through the unattached amp probes
shortest distance between the ends of the wire
as for water chemistry, the cleaner the water the more hazard there is. and depending on how the end of the wire terminates into the item, stray amps will vary (the closer the connections are to each other the less stray amps, the farther apart and bigger the connection then more stray amps).
hence, the reason why 2-wire GFCI does not cover all hazards, some potentially deadly. hence, the reason why all GFCI should be 3-wire. hence, the reason why all "bathroom" appliance should be NEMA 5- !!!
here's an experiment showing you a possible scenario that a 2-wire GFCI will not protect you, and you are possibly dead.
the cord is a non-polarized nema 1- (i polarized it with silver marker). the hot has an inline ~18k resistor. the end of the cord has eyelets soldered on to attempt to mimic real terminations of an appliance. the sink is all plastic so no amps can flow out to a EGC, the water is warm tap water (my water is heavy in minerals and filtered via a water softener, more on this at the end). from the data, the "short" in the water (w/o the inline ohms) would not trip a 15 or 20A OCPD and the GFCI is as happy as a virgin for the 1st time. the stray amps across the unattached amp probes in random location in the water indicates that amps will still flow from wire --> across water --> into the body --> through body --> back into water, and return back to wire !! so as much as some of you think amps only take path of least resistance (WRONG), it takes all paths.
i dont care to explain this elementary experiment, so you'll need to understand it for yourself. in this experiment the amps through the unattached probes would not have been enough to kill, but the scenario shows the possibility exists.
voltage across end of wire no-load

short circuit amps

wires ends in water

amps of wire in water

amps probes just in water, not attached to anything

amps flowing through the unattached amp probes

shortest distance between the ends of the wire

as for water chemistry, the cleaner the water the more hazard there is. and depending on how the end of the wire terminates into the item, stray amps will vary (the closer the connections are to each other the less stray amps, the farther apart and bigger the connection then more stray amps).
hence, the reason why 2-wire GFCI does not cover all hazards, some potentially deadly. hence, the reason why all GFCI should be 3-wire. hence, the reason why all "bathroom" appliance should be NEMA 5- !!!