This is the situation. I have not been able to find any documentation.
Wetbar in the Master bedroom, for instance.
1) AFCI protection of bedroom receptacles are required(210-12(B) Per '99 NEC).
2) GFCI protection of receptacles within 6ft of the sink, serving the countertop is required(210-8(A)(7) Per '99 NEC).
3) Wallspacing - shortened read of requirements - Wallspace measured along the wall and around corners and no more than 18" from walls and maximum hieght 5'6" shall meet the requirements.
This receptacle, installed over the countertop is included in wallspacing, due to it meeting #3 mentioned above.
An electrician excluded this from the the AFCI protected circuit. When questioned why he didn't include this 1 receptacle as one of the AFCI protected outlets, he replied, "Our instructor in class has shown papers that errors will occur with the AFCI breaker when trying to put GFCI in combination with AFCI protection". When asked for the paper, he concluded that the instructor just passed one around for all to read.
These are 2 different technologies.
Has anyone seen any documentation from any testing labs that errors could occur in the AFCI breaker when blending with GFCI protection?
Wetbar in the Master bedroom, for instance.
1) AFCI protection of bedroom receptacles are required(210-12(B) Per '99 NEC).
2) GFCI protection of receptacles within 6ft of the sink, serving the countertop is required(210-8(A)(7) Per '99 NEC).
3) Wallspacing - shortened read of requirements - Wallspace measured along the wall and around corners and no more than 18" from walls and maximum hieght 5'6" shall meet the requirements.
This receptacle, installed over the countertop is included in wallspacing, due to it meeting #3 mentioned above.
An electrician excluded this from the the AFCI protected circuit. When questioned why he didn't include this 1 receptacle as one of the AFCI protected outlets, he replied, "Our instructor in class has shown papers that errors will occur with the AFCI breaker when trying to put GFCI in combination with AFCI protection". When asked for the paper, he concluded that the instructor just passed one around for all to read.
These are 2 different technologies.
Has anyone seen any documentation from any testing labs that errors could occur in the AFCI breaker when blending with GFCI protection?