Re: GFCI all over the house
Charlie,
Let's not loose sight of the fact that a GFCI is set for the range of 4 to 6 mA and may not protect the young, old, infirm, and small people from electrocution. The threshold is high enough to prevent nuisance tripping and to protect normal sized, healthy adults.
I feel you are exaggerating the danger, even if you have a point. The graph below is based on IEC 60479, Effects of current on human beings
This applies to adults. The 'b' curve is the current where some people loose control over their muscles. The 'c1' curve is the limit where some people start getting heart problems. (The 'c2' and 'c3' indicate 5% and 50% of people respectively)
The effect of the current is more severe the smaller/lighter the victim is. Obviously, a child will be much more sensitive than an adult.
However, the GFCI will still protect the child if the current is above the threshold of the device.
This forms the basis of the European view on GFCI protection: 30mA devices are used for protection people. It is considered sufficient to save those who have a current greater than this going through them. The number of people being killed by currents too low to affect the heart, but high enough to render them unable to get away from the current is too low to be an issue.
In North America the lower voltage (120V vs 230V) means that this risk is greater and consequently the GFCI's are designed to trip at 6mA or less.
It has been mentioned before but I don't think you are picking up on the fact that a shock will be delivered before the device trips, if it trips.
The current the human body can survive depends on the time it is exposed to it. The GFCI is designed to trip very fast. I don't have the data for an American device, but the types sold here in Europe typically trip in 40ms. For this very short period of time, the body can survive a significant current. If you look at the graph above, an adult will survive 500mA or more.
I would encourage the orginal poster to install GFCIs. It will make his children significantly safer, although teaching them respect for electricity is the most important safety measure.
[ June 29, 2003, 11:01 AM: Message edited by: c-h ]