I would check the GFCI because most are rated 120v/240v not 208V. I believe they make them 208V
Sounds like hooking up the breaker isn't your biggest problem. Make room in the existing conduit or run a new one.I want to put the gfci in line with the 2 hots and a egc the conduit is full I cant pull more wire they want gfci 20 feet from pump the panel is 100 feet from where they want the gfci.
I would check the GFCI because most are rated 120v/240v not 208V. I believe they make them 208V
But if the manufacturer has not done the required UL tests in the 120/208 configuration they will not sanction it's use in that configuration and an AHJ is likely to reject it as contrary to listing.A two pole GFCI in a 120/240 volt or a 120/208 panel would work the same the gfci works on 120 volts of each leg.
Sounds like this is a customer requirement, not Code.Why do you want to install a GFCI on the pump?
A two pole GFCI in a 120/240 volt or a 120/208 panel would work the same the gfci works on 120 volts of each leg.
There is a 32V differential in potential as well as 3ph being 120* between hots vs 180* for 120/240V. GFCI may not care about that but there have been threads here re: 120V AFCI breakers not working correctly/rated for 208V service.
That has nothing to do with how a gfci works.
Which I stated, not clearly enough. The main point that I (and GoldDigger in the post before) was getting at is that a 2p GFCI breaker may not be rated or listed for 208V. Some are, like this one:
"The Siemens 2-pole GFCI circuit breaker can be installed on a 120/240V AC single phase, 3 wire
system, the 120/240V AC portion of a 240/120 volt, 3 phase, 4 wire system, or on a 208Y/120 volt, 3 phase, 4 wire system. When installed on these systems, protection is provided for 2 wire, 240V AC or 208V AC circuits; 3 wire, 120/240V AC circuits."
Irrelevant here, but noteworthy, is that the 120V 1p breakers are not listed for 120/208V.
As for the rest of my post, it was on point to the question you asked:
"how can I wire the gfci with no neutral ?"
Which I stated, not clearly enough. The main point that I (and GoldDigger in the post before) was getting at is that a 2p GFCI breaker may not be rated or listed for 208V.
Standard 2 pole breakers are only listed 120/240 yet we use them on 208 quite often.