091103-1319 EST
I agree that if a GFCI is not required, then do not use one. When not necessary it is just one more complex item to cause problems.
However, I would like to know the cause of tripping of the GFCI of the first post (OP). When conditions exist that cause a GFCI to randomly trip, or trip for a known trigger (in this case turning off the fan), but a condition for which the GFCI is not expected to trip, then it is desirable to try to determine why the GFCI is tripping. Is it an individual faulty GCFI, a design problem, or an unusual event?
In the case of this model GFCI I would not expect it to trip on typical voltage transients I have generated. And I do not think the fan motor turn-off is likely to generate transients as large as with my fluorescent ballast test. Is the particular GFCI faulty? Substituting a different GFCI (meaning a different batch of the same model or a different design) would be a typical first test. Second try bench testing the particular GFCI to see if the tripping can be caused in a different environment.
I did run a test with an MOV from the output hot to ground and cycled the ballast and there was not enough transient energy to ground to trip the Leviton GFCI. As an aside the leakage current of the GE V150LA10A MOV was about 0.05 MA with 124 V RMS 60 Hz applied. This MOV is about 1/2" in diameter. Maximum specified peak transient clamping voltage at 10 A is 340 V, minimum DC voltage at 1 MA is 184 V.
Why is it important to know why a failure occurs? Because it can determine your decision of what products to use, or how to help in the improvement of the products.
.