Until a protective device like a GFCI or RCD trips your hit with the full available fault current not just some. A GFCI does nothing to limit current until it trips.All of these devices allow some amount of current to flow before they react.
Until a protective device like a GFCI or RCD trips your hit with the full available fault current not just some. A GFCI does nothing to limit current until it trips.All of these devices allow some amount of current to flow before they react.
xFCI breakers are junk that fail while energized, with detrimental reliance on end users to push test buttons monthly.The push button AFCI or GFCI test has nothing to do with the thermal magnetic function of the breaker. That function is mechanical, while the AFCI or GFCI have an electronic function that engages a solenoid to cause the breaker to open.
So submit a proposal to make a change to UL 489. The system works the same as it does for the NEC as far as making changes.xFCI breakers are junk that fail while energized, with detrimental reliance on end users to push test buttons monthly.
I would feel better with standards that check Thermal-Magnetic function after push-button resets fail.
It may be easier to collect signatures for a congressional bill, to adopt RCD in place of xFCI, on the national level.So submit a proposal to make a change to UL 489. The system works the same as it does for the NEC as far as making changes.
However there is no practical way to check the operation of the thermal magnetic function of an installed breaker.
That would be a state's rights issue and unconstitutional.It may be easier to collect signatures for a congressional bill, to adopt RCD in place of xFCI, on the national level.
So you want the code to require us to install two devices in place of one?xFCI breakers are junk that fail while energized, with detrimental reliance on end users to push test buttons monthly.
I would feel better with standards that check Thermal-Magnetic function after push-button resets fail.
RCD has always been available as a separate circuit-breaker function, separate from thermal-magnetic breakers.
Like Roe v. Wade, RCD v. xFCI would protect the right to have an RCD in place of xFCI, and strike down state adoptions of NFPA that prohibit the right to choose.That would be a state's rights issue and unconstitutional.
So you want the code to require us to install two devices in place of one?
Just like users are require to regularly test smoke and carbon dioxide monitors.UL, ANSI, & NEC 110.3(B) make end users responsible to push xFCI breaker reset buttons that fail while energized.
Thermal-magnetic breakers have almost 100 years of successful installations without the need for 'standard checks". This is similar to the experience with thermostats and boiler/water heater safety valves.Besides the end-user test, what standard checks Thermal-Magnetic function after push-button resets fail?
But, in post 15, you appear to say RCDs prevent shocks.Until a protective device like a GFCI or RCD trips your hit with the full available fault current not just some. A GFCI does nothing to limit current until it trips.
Vehicle gauges, CO & smoke alarms have flashing idiot lights, readily visible, with audible buzzing, or chirps, not secluded behind silent equipment covers, in locked rooms, or outdoors.Just like users are require to regularly test smoke and carbon dioxide monitors.
How about vehicle warranties that require fluid monitoring?
Fuses??Its unconscionable to expect fuses to fail in the energized state
End users subject to a reasonable person standard, may regard a fuse box with circuit breakers, or fuses, as one in the same.Fuses??
I thought we were discussing the lack of testing for thermal-magnetic functions of breakers.
But you as a qualified electrician should not.End users subject to a reasonable person standard, may regard a fuse box with circuit breakers, or fuses, as one in the same.
Neither should my services, or contracts, fail to offer the required maintenance.But you as a qualified electrician should not.
Many of which come from manufacturers that have something to gain by selling product under the name of improved safety whether is fully justifiable or not. Similar to how big pharmacy sort of has big say and leads the way for rules and regulations for medical treatments and procedures. They have deep enough pockets to push their interests into becoming the rules and regulations.Remember the UL standards are much like the NEC...changed based on submitted proposals and those are acted on in a manner that is identical to that used for the NEC as the product standards and the NEC are both ANSI consensus documents covered by the same ANSI rules for the development of consensus standards.
I've responded to several electrical shock injuries during 45 years of volunteer medical rescue work. I worked that same interval as an electrician. One of the incidents my station's ambulance responded to was an employee at a school cafeteria that had been shocked by contact with a commercial (food) mixer which had been energized by damage to its flexible cord which had severed the Equipment Grounding Conductor (EGC) and faulted one of its 2 energized conductors to the frame. I responded as part of the Engine's crew because calls for pulseless resuscitation always get a manpower unit to help with Cardio Pulmanary Resuscitation while the ambulance crew initiates other care.Thats a myth, I know of no evidence to support the claim that the ma makes a difference on a 240V boost heater (fixed equipment) with a equipment grounding conductor bonding all metal parts like we're discussing.
I used to do that very thing to one of every 10 circuit breakers we installed in prebuilt communications shelters at Integrated Power Corporation (IPC). We just applied the loads that the manufacturer gave as 2 points on the trip curve, I don't remember which 2 points we used, and timed the opening with a laboratory multimeter with a timing function and memory. What was missing from that testing? Can you explain it so that a factory floor test and installation technician will understand?However there is no practical way to check the operation of the thermal magnetic function of an installed breaker.
Thanks for the feedback I appreciate the discussion, since there is no UL GFCI standard for a 240V delta system, for the OP I was comparing the protection offered by a regular breaker to a Residual Current Device (RCD).So if a Residual Current Detector (RCD) will tolerate 30 mA of current escape from the circuits current carrying conductors and a GFCI will tolerate no more than 5 mA of current escape how can anyone say that RCDs are the better protective device for human safety from electrocution? Please clearly explain what I didn't understand about the postings that said that RCDs are superior to GFCIs. I've never worked on anything that had RCD protection in the US. I saw a couple of them during a project in Argentina but that's as close as I ever got. I'm not claiming that I know but the difference between the 2 sets of numbers offered doesn't seem to support the superiority of RCDs.
That 5 or 30 mA is only a direct personnel protection feature when someone comes into contact with something that is energized.I've responded to several electrical shock injuries during 45 years of volunteer medical rescue work. I worked that same interval as an electrician. One of the incidents my station's ambulance responded to was an employee at a school cafeteria that had been shocked by contact with a commercial (food) mixer which had been energized by damage to its flexible cord which had severed the Equipment Grounding Conductor (EGC) and faulted one of its 2 energized conductors to the frame. I responded as part of the Engine's crew because calls for pulseless resuscitation always get a manpower unit to help with Cardio Pulmanary Resuscitation while the ambulance crew initiates other care.
Because the City's Lion's club had just given us the first Automated External Defibrillator (AED) to be carried by a basic ambulance in our entire region the victim survived. [When we went to the Lion's club next meeting to announce the results of their donation they clapped, cheered, and cried!]
What's my point? It is axiomatic in emergency medicine that 30 mA through the chest cavity will cause cardiac fibrillation which is inevitably fatal if a defibrillator is not applied within 10 minutes and that for the patient to have a truly positive outcome, meaning a full recovery, it must be applied within 6 minutes of onset and CPR was begun within 3 minutes. So if a Residual Current Detector (RCD) will tolerate 30 mA of current escape from the circuits current carrying conductors and a GFCI will tolerate no more than 5 mA of current escape how can anyone say that RCDs are the better protective device for human safety from electrocution? Please clearly explain what I didn't understand about the postings that said that RCDs are superior to GFCIs. I've never worked on anything that had RCD protection in the US. I saw a couple of them during a project in Argentina but that's as close as I ever got. I'm not claiming that I know but the difference between the 2 sets of numbers offered doesn't seem to support the superiority of RCDs.
"Appliances identified in 422.5(A)(1) through (A)(7) rated 150 volts or less to ground and 60 amperes or less, single- or 3-phase, shall be provided with Class A GFCI protection for personnel. Multiple Class A GFCI protective devices shall be permitted but shall not be required.
(7)Dishwashers”