It's the surge suppressor(s). We've talked about this here before, you can't use surge suppressors on a GFCI circuit or with a GFCI receptacle. It's going to cause random tripping. Nothing to do with cheap or failing surge suppressors either, except maybe the cheap ones that don't do much will work.
From a surge suppressor design point of view, I've ALWAYS thrown a gas discharge tube in series with any MOV tied line to ground, or neutral to ground. GDTs have "no" leakage current until they reach breakdown voltage, which then lets the MOV dump as much current as it can handle. MOV ages, gets damaged, etc, there isn't an issue with tripping. Also reduces the unfriendly tingle from aging equipment people have removed the ground prong from.
While GDTs will have lower leakage than MOVs, once you have a GDT I'm not sure what the advantage would be of putting an MOV in series with it. The resulting response time will be limited by the slower response of the GDT that Russs57 has mentioned. But the current handling and ability to dissipate the surge energy will be limited by the MOV because it will have a much larger share of the voltage drop once the GDT breaks over. So I don't see the advantage of the of the series combination over having the GDT alone.From a surge suppressor design point of view, I've ALWAYS thrown a gas discharge tube in series with any MOV tied line to ground, or neutral to ground. GDTs have "no" leakage current until they reach breakdown voltage, which then lets the MOV dump as much current as it can handle. MOV ages, gets damaged, etc, there isn't an issue with tripping.
MOV's get damaged over time and leak more and more. They really should have a thermal switch in series along with a LED to let you know when thermal switch has made them inactive.
Was somewhat what I was thinking, doesn't seem to be an advantage of putting those two items in series with one another. Your needs can be one or the other but can't really get best of both at the same time.While GDTs will have lower leakage than MOVs, once you have a GDT I'm not sure what the advantage would be of putting an MOV in series with it. The resulting response time will be limited by the slower response of the GDT that Russs57 has mentioned. But the current handling and ability to dissipate the surge energy will be limited by the MOV because it will have a much larger share of the voltage drop once the GDT breaks over. So I don't see the advantage of the of the series combination over having the GDT alone.
Now having a shunt GDT, a series impedance such as an inductor, and then a shunt MOV to form a "pi" network can be very effective as described in the app note linked below. The MOV reacts quickly to clamp the beginning of the surge while the current is limited by the series impedance, and then the GDT breaks over and limits the pass thru voltage to low values in spite of very high current levels.